Titus A Duxass wrote:Makes no odds if it's 110 or 240 as long as it can cope with the current.
Of course it does - you wouldn't use a cable rated at 12v would you? Voltage is a measure of electrical 'pressure'; it's ability to force it's way to it's objective (usually ground in the shape of neutral or earth). Insulation is constructed in order to (amongst other things)
guarantee resistance to this pressure up to a specified maximum amount and is assigned a BS or BSEN number to verify it's particular voltage ceiling. Applying a voltage to a cable in excess of it's insulation's capability is destructive, it insidiously and slowly breaks down the insulation over time.
This however may be besides the point, a yellow 110v cable may well be rated for 240v. You need to find the cables actual BS number which (if you're lucky) will be moulded into the outer sheath. Here's two 'Arctic' cables, one yellow, one blue
http://www.discount-electrical.co.uk/pr ... 0f81c4082f" onclick="window.open(this.href);return false;
http://www.discount-electrical.co.uk/pr ... -100m-reel" onclick="window.open(this.href);return false;
Both are voltage rated to BS 6500 which is 300/500 volt. However, this standard was introduced in 2000 so if your cable is older than that it will only comply with an earlier BS which may well not cover it for the higher voltage. Basically, find the BS and google it.......
Then make sure the conductors are a minimum of 2.5mm c.s.a copper.
There are other standards that apply to flexible cables such as resistance to chemicals, UV radiation, mechanical damage etc but I'm not going there!!