3 way fridge vents size! Huge!!!

The Tardis factor (interiors , awnings, roofs etc)

Moderators: User administrators, Moderators

jiffies
Registered user
Posts: 163
Joined: 20 Sep 2009, 19:11
80-90 Mem No: 7506
Location: Southampton

3 way fridge vents size! Huge!!!

Post by jiffies »

Hi
Just bought a new Dometic RM4181 3 way fridge for the van. I’ve been informed it need 2 x vents going externally out of the van. The cut out holes are huge H 156mm W 451mm. I don’t really want two dirty great holes as large as this. Anybody else used smaller vents & what would be the consequence?

Could I not have a large inward vent inside the van as shown in the bottom example (Not mine by the way) then only one of the outside

Cheers

Jiffies

User avatar
eatcustard
Registered user
Posts: 1817
Joined: 27 Oct 2008, 07:26
80-90 Mem No: 6062
Contact:

Re: 3 way fridge vents size! Huge!!!

Post by eatcustard »

My Leisure drive has only one vent (the higher one)
and had the Electrolux version fitted.

It does not say you must have both, but for best performance have both
https://www.penguinjones.co.uk" onclick="window.open(this.href);return false; PM me for your 10% discount

User avatar
windysurfer
Registered user
Posts: 996
Joined: 14 Jun 2007, 18:58
80-90 Mem No: 3805
Location: Lancashire

Re: 3 way fridge vents size! Huge!!!

Post by windysurfer »

I just fitted an internal vent with a thermostatically controlled fan for the top vent and an air gap at the bottom

Image

Image
If Carlsberg made Coachbuilts...........Image T4 Karmann Colorado

Jill
Registered user
Posts: 89
Joined: 12 Jun 2006, 16:54
80-90 Mem No: 2776
Location: Andover, Hampshire

Re: 3 way fridge vents size! Huge!!!

Post by Jill »

If you are planning to use gas as a power source, then yes, you do need external vents. Carbon Monoxide has no smell, but the blood will take it up in preference to oxygen, thereby killing you.

Don't cut corners with gas in your van.

Cheers Jill
Member 2776.

If it ain't broke, don't fix it!

Do not meddle in the affairs of Dragons, as you are crunchy and good with ketchup!

Preserve wildlife-pickle a Traffic Warden!

User avatar
windysurfer
Registered user
Posts: 996
Joined: 14 Jun 2007, 18:58
80-90 Mem No: 3805
Location: Lancashire

Re: 3 way fridge vents size! Huge!!!

Post by windysurfer »

Jill wrote:If you are planning to use gas as a power source, then yes, you do need external vents. Carbon Monoxide has no smell, but the blood will take it up in preference to oxygen, thereby killing you.

Don't cut corners with gas in your van.

Cheers Jill

I think we're referring to vents to allow a good flow of air over the cooling fins at the rear of the fridge.The exhaust gases from the fridge must be vented outside.

It's an excellent idea to use a carbon monoxide in your van as well
If Carlsberg made Coachbuilts...........Image T4 Karmann Colorado

User avatar
jamesc76
Registered user
Posts: 6241
Joined: 14 Oct 2005, 14:42
80-90 Mem No: 1186
Location: Nottingham
Contact:

Re: 3 way fridge vents size! Huge!!!

Post by jamesc76 »

I fitted just the top one and leave the cover on it unless its a silly hot day!
DJ at Dubdayz Summerfest
Now cutting about in an LT35 MWB

User avatar
Ian Hulley
Registered user
Posts: 12661
Joined: 11 Oct 2005, 08:08
80-90 Mem No: 1323
Location: Wirksworth, Derbyshire ... or at t'mill

Re: 3 way fridge vents size! Huge!!!

Post by Ian Hulley »

The other issue is condensation which forms on the panel behind the fridge and runs down, collects and rots out the lower sill panels. I put the 2 vents in my van, but have the lower one blocked up in winter. Then again I wanted my former panel van to look and work like a camper not t'other way round.

Ian.
The Hulley's Bus
1989 2.1DJ Trampspotter
LPG courtesy of Steve @ Gasure

jiffies
Registered user
Posts: 163
Joined: 20 Sep 2009, 19:11
80-90 Mem No: 7506
Location: Southampton

Re: 3 way fridge vents size! Huge!!!

Post by jiffies »

The bottom external vent is a MUST. This allows cold air in & more importantly carbon monoxide out.
The only issue I have is that the Dometic vents are too large to fit where they should be for the fridge to be at its most efficient. The top vent wont fit in the panel directly below the window, then there is the thin recesss level with the door handles. So the only place it can pysicallt fit is the next panel down. If you then instal the bottom vent so that it is only just above the van finished floor level this only leaves 265mm between the two vents. It just looks all too invasive.
All I'm looking at doing is ventinmg the top vent some other way
Options:
Venting through pipe to external van louvre vents
Using a smaller rectangular fridge vent (Although the cheaper ones certainly dont look water tight)
Have a small custom vent cover made so i can drill a hole/slots in van that the cover fits over and stops rain etc. (Possibly stainless steel- Sort of similar to a leadlamp eyebrow type design) Anyone ever seen this sort of thing?

User avatar
Nicola&Tony
Registered user
Posts: 2674
Joined: 01 Nov 2006, 18:18
80-90 Mem No: 3095
Location: Wallsend, Tyne & Wear

Re: 3 way fridge vents size! Huge!!!

Post by Nicola&Tony »

jiffies wrote:The bottom external vent is a MUST. This allows cold air in & more importantly carbon monoxide out.

Surely any carbon monoxide that is produced when the fridge is running on gas goes up the chimney and out of the flu? Afaik Autosleeper only fitted one vent when they installed Electrolux fridges in t25's, but it's a type which has an integral flu. We often sleep with the fridge running on the lowest gas setting overnight and a carbon monoxide alarm not very far away.

Tony
Looking for: window apertures for side windows, at the back of the van

T25; 1985; RHD; 1.9DG petrol / LPG; white Autosleeper high-top; Looking rusty again!

LT31; 1993; RHD; 2.4L petrol; high-top; diy camper project.

User avatar
Ian Hulley
Registered user
Posts: 12661
Joined: 11 Oct 2005, 08:08
80-90 Mem No: 1323
Location: Wirksworth, Derbyshire ... or at t'mill

Re: 3 way fridge vents size! Huge!!!

Post by Ian Hulley »

Nicola&Tony wrote:
jiffies wrote:The bottom external vent is a MUST. This allows cold air in & more importantly carbon monoxide out.

Surely any carbon monoxide that is produced when the fridge is running on gas goes up the chimney and out of the flu? Afaik Autosleeper only fitted one vent when they installed Electrolux fridges in t25's, but it's a type which has an integral flu. We often sleep with the fridge running on the lowest gas setting overnight and a carbon monoxide alarm not very far away.

Tony

Totally agree.

Ian
The Hulley's Bus
1989 2.1DJ Trampspotter
LPG courtesy of Steve @ Gasure

jiffies
Registered user
Posts: 163
Joined: 20 Sep 2009, 19:11
80-90 Mem No: 7506
Location: Southampton

Re: 3 way fridge vents size! Huge!!!

Post by jiffies »

Apologies!

Text from instruction manual:

Lower vent allows any leaking unburnt gas to escape. If there is no lower vent then a 40mm dia. hole in van floor is required

Flue gases are dispersed through upper grill vent

Therefore both are required as they wouldnt sell two otherwise. I just need a better solution for the top one!!

User avatar
Ian Hulley
Registered user
Posts: 12661
Joined: 11 Oct 2005, 08:08
80-90 Mem No: 1323
Location: Wirksworth, Derbyshire ... or at t'mill

Re: 3 way fridge vents size! Huge!!!

Post by Ian Hulley »

Is there a separate flue on this fridge ?

Ian.
The Hulley's Bus
1989 2.1DJ Trampspotter
LPG courtesy of Steve @ Gasure

User avatar
windysurfer
Registered user
Posts: 996
Joined: 14 Jun 2007, 18:58
80-90 Mem No: 3805
Location: Lancashire

Re: 3 way fridge vents size! Huge!!!

Post by windysurfer »

Ian Hulley wrote:The other issue is condensation which forms on the panel behind the fridge and runs down, collects and rots out the lower sill panels. I put the 2 vents in my van, but have the lower one blocked up in winter. Then again I wanted my former panel van to look and work like a camper not t'other way round.

Ian.

Are the hardboard panels removed from behind your fridge then Ian?
There still in place on mine which should stop\help with the condensation problem.
If Carlsberg made Coachbuilts...........Image T4 Karmann Colorado

User avatar
Nicola&Tony
Registered user
Posts: 2674
Joined: 01 Nov 2006, 18:18
80-90 Mem No: 3095
Location: Wallsend, Tyne & Wear

Re: 3 way fridge vents size! Huge!!!

Post by Nicola&Tony »

jiffies wrote: . . . I just need a better solution for the top one!!

How about fitting (1) a bottom vent or drop-out hole (2) an upper vent which vents inside the van (like windysurfer did) (3) a flue kit for the carbon monoxide:
http://www.caravantech-shop.co.uk/produ ... c-flue-kit

Tony
Looking for: window apertures for side windows, at the back of the van

T25; 1985; RHD; 1.9DG petrol / LPG; white Autosleeper high-top; Looking rusty again!

LT31; 1993; RHD; 2.4L petrol; high-top; diy camper project.

User avatar
Team28crew
Registered user
Posts: 190
Joined: 29 Jul 2008, 20:26
80-90 Mem No: 5770
Location: Wirral

Re: 3 way fridge vents size! Huge!!!

Post by Team28crew »

Just an idea so sorry if its carp but could you not fit the lower vent into the floor behind the fridge, that way you only have one vent on the side of your van. This is the set up on my Leisure drive conversion, flue out at the top and a vent under the rear of the fridge.
1986 1.9DF LeisureDrive Hi Top LPG'd by Gasure

Locked