Extract from workshop manual:
Upon switch on positive control voltage is applied from the
battery across F2 and terminal A5 to the electronics of the
control unit.
- operating indicator light H1 illuminates.
- glowing is activated via relay K1 and circulation pump
via relay K2.
- after pre-glowing (approx. 30 sec) a cycled voltage is
applied to connector C2 via transistor V108. From
connector C2 dosing pump Y1 is triggered across
temperature fuse F3.
- the safety period of approx. 90 sec commences.
- after fuel priming time (approx. 5 sec) the combustion
air fan motor M1 is started in full load mode via relay
K4.
If there is a "flame" condition during the safety period,
flame sensor B1 signals "bright" and relay K1 deenergises.
The safety period is reset and the glow plug is
switched off. This procedure requires approx. 15 sec for
normal ignition.
Repeat start:
If there is a "no flame" condition during the safety period,
there will be an automatic restart attempt with a 30 sec
run-down involving glowing, pre-glowing (approx. 30 sec)
and safety period (approx. 90 sec). This start-up pattern is
also applicable for a re-activation during controlled
operation