Out of level problems are more of a problem on the old square boiler enclosure - these are very rare now.
Check that there is adequate airflow over the cooling fins also.
From the Dometic service manual:
After the unit has been operating for
approximately one hour, carefully touch the unit
at the boiler box and the absorber area. These
areas should be approximately the same
temperature, regardless of the ambient
temperature. Equal heat between the boiler and
the absorber indicates the fluid circulation within
the unit is good.
Under normal operation the temperature at
the absorber coils (A) and the boiler (B)
should be approximately the same. If the
temperature at the absorber coils (A) is
much hotter it indicates loss of refrigerant
and the cooling unit must be replaced. If
the temperature at the boiler (B) is very hot
and the absorber coils (A) are cool it indicates
that the refrigerant is not circulating properly.
This could indicate:
A. Liquid trapped in the evaporator sections,
caused by out-of-level operation for a
period of time. Resetting the refrigerator
to a level position will not necessarily
correct the problem as liquid can remain
trapped even after level is corrected.
Shut off the heat source and let the
system cool down, then re-start it and
observe the temperatures at A and B
again after several hours. If the same
condition exists it could indicate:
B. A permanent blockage within the boiler
pump tube, caused by too much heat
applied to the burner (oversized orifice
or heating element) or prolonged operation
of the unit when out-of-level or with
restricted ventilation. This type of
blockage consists of hard deposits inside
the boiler pump tube. This condition is
not repairable and the cooling unit must
be replaced.