Would someone please explain in simple terms what this means below; DNO, TNS, UKPN, SPD etc?
Also the C2's are:
Remedial action required for 40 Thanet Road
Also the C2's are:
Remedial action required for 40 Thanet Road
RCD protection required
Bathroom light fitting is not sufficiently IP Rated
Cables not securely fixed
Along with the combustibility and age of the existing consumer unit, I suggest that a new dual RCD board is fitted with SPD (this can be opted out of by the landlord but I would need instruction to do so and this would be included as comments on the paperwork). While doing this, all cables in the basement can also be securely fixed. In addition to this, I will change the light fitting to a sufficiently IP rated fitting for safety.
DNO requests –
- TNS earthing system is not offering decent earth reading, I can deal with UKPN with regards to instruction to change this earthing arrangement to PME as there is sufficiently low resistance between the Live and Neutral conductors coming into the property.
- Main Fuse requires inspecting at the very least and most likely changing, this will also require talks with the DNO
Total price for all of the above would be £1072.5 (savings of £100 could be made by removing the SPD as this is included in this quote)
This does not take account for the C3 recommendations included in the report.